PID on a ControlLogix: the Loop Update Time, the Task and the Tieback
A PID instruction on a 1756-L83E executes on every scan of the routine that holds it, and it never once asks the controller what time it is. Its integral and derivative terms are built from .UPD, the loop update time you typed on the Configuration tab, and not from the gap since the last execution. 1756-RM018A says it in one sentence in the opening paragraph of the instruction: the .EN bit is set when EnableIn goes true, the PID instruction does not use a .DN bit, and the instruction executes every scan as long as EnableIn is true.
So the whole job is making the real interval match the number.
Put the PID in a periodic task, set .UPD equal to the task period in seconds, and never gate the instruction behind a conditional rung.
Everything below is how to do that, or what happens when you do not.

.UPD and the tieback range are highlighted because both are configuration fields that people leave at whatever the wizard put there. One decides the integral action; the other decides whether the transfer out of hand is smooth.
The instruction has no clock, and that is the whole trap in this set
Every process instruction in this group behaves differently depending on when it is called, and the classic PID is the bluntest example because it does not even try to measure. A PIDE at least has a DeltaT output you can go and look at. In periodic timing mode inside a periodic task it takes the task’s period; in an event or continuous task it takes the elapsed time since the previous execution, truncated to whole milliseconds, so 10.5 ms is used as 10 ms. The PID instruction has no such member. It has .UPD, a REAL in seconds, and it believes it.
That asymmetry is worth holding on to, because it decides the fix.
If a PIDE, a TOT, an SCRV or an RLIM is called at an uneven rate, the instruction knows and the arithmetic follows the real interval — 1756-RM006 still calls that a discontinuity, and lists an instruction skipped in a scan and an instruction executed twice in a task as two of the causes, but at least the block is working from something measured. If a PID is called at an uneven rate, nothing anywhere in the controller knows. The reset action is computed as though 250 ms passed, twelve times in a row, while the clock says 3.44 seconds went by rather than 3.00.

Both loops have .UPD at 0.25 and identical gains. The green trace is the same instruction in a continuous task behind a TONR done bit, where one long scan at execution five costs 101 ms and nothing recovers it.
Set .UPD
A .UPD that is merely wrong produces no fault at all, and no status bit anywhere compares the two against each other. Nothing else on this page is as cheap to check or as expensive to miss.
The number is a promise the program has to keep.
Three ways to call it, and what each one costs you
1756-RM018A names all three, in order of how much it likes them.
The default answer is a periodic task. Set the task period, set .UPD to the same number in seconds, put the PID on an unconditional rung, and stop thinking about it. A 250 ms task means .UPD = .25. The manual’s other requirement here is easy to skip and expensive: the analogue input carrying the PV should be produced at least five to ten times faster than the task runs, so a 250 ms loop wants the module at something like 25 to 50 ms. An input module left at an RPI equal to the task period gives the loop the same sample twice as often as it gives it a new one, which shows up as derivative noise and as an oscillation whose period does not move when you halve the gain. Where those counts come from and what the module actually does with them is covered in reading a 4-20 mA transmitter into a 1756-IF8.
Where you cannot have one, the fallback is a continuous task with a timer. Run a TONR with its preset equal to .UPD and gate the PID on the done bit. The manual calls this “somewhat less accurate” and adds a condition that is the real limit: only use it where the loop update time is several times longer than the worst-case execution time of your continuous task. A 250 ms loop inside a continuous task that occasionally takes 180 ms is not several times anything. If you do not know your worst case, PLC scan time and cycle time is where to measure it before you decide.
Then there is the rolling timestamp, which is the one the manual calls the most accurate and almost nobody uses. A 1756 analogue input module publishes a .RollingTimestamp that counts 0 to 32,767 ms and advances every time the module takes a real-time sample. Watch it; execute the PID exactly once each time it changes; set .UPD equal to the module’s RTS time. Because the sample and the execution are now tied to the same event, the loop’s idea of elapsed time is the module’s, which is quartz rather than software. Run the logic that watches the timestamp faster than the RTS period so you cannot miss one — the manual’s own example is an RTS of 250 ms watched from a 100 ms periodic task.
That last method earns its trouble on one kind of loop: the fast one. On a level loop updating once a second, twenty milliseconds of jitter is two percent and invisible; on a tension loop at 20 ms it is the whole interval.
Pick by the ratio, not by the instruction.
What the tieback operand is actually for
The tieback is the fourth operand on the instruction and most projects have a literal zero sitting in it.
It exists for one piece of hardware: a hand/auto station.
The station sits between the controller output and the final element and can be switched to bypass the controller entirely. When it is in hand, somebody is turning a knob and the valve is following the knob rather than the PLC. The tieback operand is where you bring that knob position back into the controller, usually as another analogue input on the same card, so the loop can watch what the valve is doing while it is not the one doing it.
Two modes use it, and they are not the same mode.
Software manual, .SWM, bit 26 of .CTL, uses .SO — a set output percentage typed from the faceplate. Manual, .MO, bit 24, uses the tieback, scaled to 0-100% by .MINTIE and .MAXTIE exactly the way the PV is scaled by .MINI and .MAXI. The two bits are independent, so both can be on at once, and the answer is not the one people expect: .MO wins.
1756-RM018A prints that as an IMPORTANT note rather than burying it.

Same loop, same gains, same transfer. The difference is whether the tieback operand was a real analogue input or the literal 0 that the instruction was entered with.
Here is why it matters at the moment of transfer. The PID back-calculates the integral accumulation term needed to make CV come out equal to .SO in software manual, or equal to the tieback in manual, so that when the mode flips to auto the output starts from where the process already was. With the tieback at zero, the block dutifully back-calculates the integral term required to produce zero percent — and then auto starts from zero percent, or from .MINO if you set one, which on a gas valve at 61% is a cold dryer and a shift supervisor. The same machinery works without integral action: if .KI is zero the instruction modifies .BIAS instead to make CV track the tieback, and keeps that .BIAS value when auto resumes.
Setting .NOBC turns that off. There is almost never a reason to.
The other bumpless transfer, the one that happens at power-up
Two operands at the end of the instruction do a different job: Inhold bit and Inhold value.
Configure the 1756 analogue output channel with Hold for initialization ticked. When the controller goes to Program or loses the connection, the module drives the output to its configured fault value; when the controller comes back, the module holds the output where it is until the value arriving from the controller matches what the channel is using to within 0.1% of span, then ramps across using the .BIAS term. The channel publishes two things back: an InHold status bit and a data readback. Wire the status bit to the PID’s Inhold bit operand and the readback to Inhold value, and on the first scan after a restart the instruction moves the readback into CV and re-initialises around it. The module sees its own number come back, drops InHold, and the loop takes over.
Four operands, no logic, and a restart that does not slam a valve.
The output side of that chain is worked through in an analogue output that drives a valve. Read it before you pick the module’s fault value, because that value is what the channel sits at while the loop catches up.
Before you touch a gain
A loop that hunts gets retuned, because retuning is the thing everyone knows how to do.
Check three numbers first, and none of them is a gain.
What task is the PID in, and is its period the same number as .UPD? What is the RPI on the analogue input carrying the PV, and is it at least five times faster than that period? Is the PID on a rung that is ever false, or inside a JSR that is ever skipped? A PID called four times out of five scans integrates at four-fifths of the rate the gains describe, and no amount of tuning will find that.
The cross-reference takes a minute and settles it.
One more that costs an hour the first time. If you set .MAXO equal to .MINO on the ladder PID, the instruction quietly resets them to 100.0 and 0.0, which means the clamp you thought you had entered is not there. And guard the PV before the instruction runs: 1756-RM018A repeats the same warning on four consecutive pages, that an INF or NAN reaching the PID locks it up with invalid internal floating point values, and suggests gating the rung on S:V among other things.
Put PV, SP and CV on one trend at the task rate and watch a transfer out of manual before you change anything — PLC trend chart settings and monitoring covers getting the sample rate right, and the transfer tells you more in ten seconds than an hour of watching the loop run.
And if the block is a PIDE rather than a ladder PID, go and check the units before the gains. The number that means a 48 second reset differs by a factor of sixty between the two instructions, which is worked through in setting up a PID in Studio 5000.