Two OEM CompactLogix packers both on 192.168.1.x, second one can't join the network

2 Posts
2 Users
0 Reactions
0 Views
(@priya87)
New Member
Joined: 1 year ago
Posts: 0
Topic starter   [#157]

We bought a second case packer from the same OEM and it turned up on the same addresses as the first. CompactLogix 5069-L320ER at 192.168.1.10, PanelView at .11, two PowerFlex 525 and a Cognex reader. I checked, both PLCs really do sit on .10.

Packer 1 is on the plant network with FactoryTalk View SE, the historian and the line 3 PLC all talking to it. I plugged packer 2 in on Monday and packer 1 went unstable, SE lost its tags and the produced tag went to 16#0204. Pulled the cable and everything came back.

I've asked the OEM for a re-addressed program and they quoted three days of engineering plus a site visit. Do we really re-address a whole machine? Packer 3 is on order. Is there a way to leave them both on .10 and still have SE see them as two machines?


Advertisement

   
Quote
(@ollyb)
New Member
Joined: 1 year ago
Posts: 0
 

We ship every machine on 192.168.1.x and I'll admit its on purpose, the test bench and the drawings stay the same that way. Most end users drop a NAT box between the machine and the plant. Did the quote actually say re-address, or did nobody mention NAT? Ask them what they do for other multi-machine sites.



   