(@eddieb)
New Member
Joined: 1 year ago
Posts: 0
Topic starter   [#77]

Hi everyone, case packer, 1769-L33ER with a PanelView Plus 7 on the same controller. Operators say the screens have gone sluggish, button presses take a second to show, and only when the machine is running at full rate. No faults anywhere.

T_Fast, the 5ms periodic task that does the flight tracking, has Overlap Count climbing on the Monitor tab, about 3 a second at full rate and zero when idle. We added a second PowerFlex 525 and tracking for a second lane about a month ago, which is roughly when it started. I doubled the RPI on the two drives from 20ms to 40ms and restarted the PanelView, no change.

Is the built in Ethernet port on the L33ER the bottleneck with the extra drive, or any thoughts?


Advertisement

   
Quote
(@carav9)
New Member
Joined: 1 year ago
Posts: 0
 

Not the port. Overlap count going up means the 5ms trigger is arriving before the previous pass of T_Fast is done. What's the task's watchdog, what priority, and what's in it, ladder or ST? And which task does the second lane's tracking run in, the same 5ms one?


Advertisement

   
ReplyQuote
(@eddieb)
New Member
Joined: 1 year ago
Posts: 0
Topic starter  

Watchdog 500ms, priority 5, ladder, about 30 rungs of flight tracking per lane, both lanes in T_Fast. So doubling the lanes doubled what's in a 5ms task. Max 6.8ms is over 5. I see it now, I think.



   
ReplyQuote
(@rsdave)
Trusted Member
Joined: 2 years ago
Posts: 65
 

Periodic tasks always win over the continuous task, and comms live off the continuous task's time slice. Starve that and the PanelView starves.



   
ReplyQuote
(@carav9)
New Member
Joined: 1 year ago
Posts: 0
 

Two things stacked. T_Fast running up to 6.8ms in a 5ms period runs past the next trigger whenever a scan goes long, overlap, and it takes priority every time. The continuous task gets what's left, and the System Overhead Time Slice that serves the PanelView comes out of that. That's your sluggish buttons, and no fault because nothing fails.

Fit the period to the work, not the other way round. Max 6.8ms, so 10ms with margin, and check the tracking still resolves at 10ms, it should. Or split lane 2 into its own 5ms task offset from the first, if 5ms is really needed. A CODESYS or TIA cyclic task does the same. Writeup on period versus execution time: https://plctr.com/understanding-plc-scan-time-and-cycle-time/



   
ReplyQuote
(@eddieb)
New Member
Joined: 1 year ago
Posts: 0
Topic starter  

Set T_Fast to 10ms. Overlap count stayed at 0 through a full shift at rate, max scan 6.9ms. PanelView buttons respond straight away. Flight tracking is fine at 10ms, worst case position error at 60 cases a minute is under 2mm, checked it at the reject gate.

So two lanes of tracking in a 5ms task that needed up to 6.8ms, overlapping, and the continuous task and the HMI comms got whatever was left. Period to 10ms and that's all it took.

Not sure about the RPI on the drives, I left them at 40ms. Probably should put them back to 20ms, nobody noticed either way.

Thanks carav9 and rsdave.



   
ReplyQuote
(@rsdave)
Trusted Member
Joined: 2 years ago
Posts: 65
 

Leave the drives at 40. Fewer packets for nothing.



   