EtherNet/IP I/O drops 16#0204 about five minutes after every switch reboot

3 Posts
2 Users
0 Reactions
0 Views
(@ines31)
New Member
Joined: 1 year ago
Posts: 0
Topic starter   [#123]

Replaced an old unmanaged switch under a ControlLogix, 1756-L81E with a 1756-EN2T, for an IT-supplied Cisco IE3300 last week. Hanging off it are two 1794-AENT, three 1734-AENTR and four PowerFlex 525.

Every time that switch reboots, and IT rebooted it twice doing firmware, the I/O is fine for about five minutes and then every rack drops 16#0204 inside the same minute, drives included. Kepware on the same VLAN never drops, which is the bit I can't explain.

On a hunch I turned IGMP snooping off and the drops stopped, but IT put it straight back on because it's in their standard config. Swapped the EN2T for a spare and that changed nothing either. So it's a switch setting, I'm just not sure which one. Any ideas what to ask IT for?


Advertisement

   
Quote
(@northbay)
New Member
Joined: 1 year ago
Posts: 0
 

Kepware is TCP, class 3, it doesn't care. Your I/O is multicast. Two things: is there an IGMP querier on that VLAN, and what's the snooping group timeout. Ask IT for the output of show ip igmp snooping, they'll have it.



   
ReplyQuote
(@ines31)
New Member
Joined: 1 year ago
Posts: 0
Topic starter  

> is there an IGMP querier on that VLAN

IT says "the router does that". The VLAN is layer 2 only, no SVI, nothing routes it. The show output says Querier: none. Group membership timeout 260 s, though I'm not sure that's the default.



   