Hi everyone,
Filler on line 2. PanelView Plus 7 running FactoryTalk View ME, CompactLogix 5370 L30ER behind it on V32. Operators type a fill setpoint on the Fill screen, the number takes, then about a second later it goes back to 50. Every single time. They've been running the line by holding the button down half a second early, which isn't great.
I power cycled the panel twice, once with the PLC as well, and that changed nothing, so then I checked the numeric input object and it does point at Fill_SP_1. Watching the tag online in Studio 5000 it goes to whatever they type and then straight back to 50, so the panel's writing it fine.
I think there must be a retentive setting I'm meant to turn on for that tag so it holds? Or is something in the program putting 50 back over the top of it every scan, because I'm not sure where else to look?
Design tab or runtime tab when you watched it? And is that a Numeric Input Enable or a Numeric Input Cursor Point? If FactoryTalk Security is on, which user is the runtime logged in as, and has that user got write.
Runtime, on the panel itself. Numeric Input Enable. Default user, no security set up on that panel as far as I know. The other setpoints on the same screen hold fine, it's only Fill_SP_1 and Fill_SP_2 that revert.