Remote view of a PanelView Plus 7 line HMI from home, IT refuses any port forward

3 Posts
2 Users
0 Reactions
0 Views
(@rookie_ray)
New Member
Joined: 11 months ago
Posts: 0
Topic starter   [#170]

First year here and I'm still finding out what we've got, because almost none of it is written down. Management want to see the line 2 HMI from home, mostly production counts and alarms. It's a PanelView Plus 7 on a CompactLogix 5380, one unmanaged switch, and the plant network sits on its own range behind a firewall IT look after.

So I asked IT to forward the VNC port on the terminal and got a flat no, and no to 3389 to the engineering PC either, with nothing beyond "not happening". Someone on my shift said TeamViewer, so I tried the free one for an hour and IT saw it and blocked it the same day. They won't hear of anything coming in.

Is a port forward really that bad if its only a viewer? Or any ideas for a way of doing this that IT would actually say yes to, because I'd rather not go back with the same ask twice?


Advertisement

   
Quote
 suel
(@suel)
New Member
Joined: 2 years ago
Posts: 0
 

Yes, it's that bad. A forwarded VNC port on a terminal is on Shodan inside a week, and the terminal has no lockout. IT were right and short with you, both.

What does the plant firewall allow outbound? Anything at all on 443?



   
ReplyQuote
(@rookie_ray)
New Member
Joined: 11 months ago
Posts: 0
Topic starter  

Outbound 443 is open, that's how the engineering PC gets its updates. Nothing else that I know of. So if the box inside calls out that's allowed, and nothing calling in is. Might be something to work with there.



   
ReplyQuote