[Solved] New ET 200SP station, IM 155-6 red ERROR, every module shows missing

6 Posts
3 Users
0 Reactions
110 Views
(@fee_m)
Trusted Member
Joined: 1 year ago
Posts: 33
Topic starter   [#39]

Morning all. First rack I've built on my own, so go easy. ET 200SP for a new conveyor section, IM 155 6 PN ST and six modules, all bought as parts and clicked onto the rail. Config done in TIA V18 to match and downloaded to the 1515 that runs the line.

IM has ERROR solid red. Every module shows a red X in device view and the buffer says something like "Backplane bus error" on the station, then module not present for each slot. The IM itself is reachable, I can see it in accessible devices with the right name. I power cycled twice, put a new PROFINET cable on and reseated every module, and none of that changed a thing.

My guess is the IM firmware is too old for the modules, they're all new. Can that be it? Or is it something about clicking a rack together out of loose parts that I've got wrong, I guess that's more likely than firmware.


Advertisement

   
Quote
(@dieter_k)
Eminent Member
Joined: 2 years ago
Posts: 20
 

Photo of the right hand end of the rail, after the last module. And the firmware number off the IM label. Firmware is rarely it, but post it anyway.


Advertisement

   
ReplyQuote
(@fee_m)
Trusted Member
Joined: 1 year ago
Posts: 33
Topic starter  

Firmware on the label is 4.2. Photo attached. After the last module there's just empty rail, the six modules and then nothing.



   
ReplyQuote
(@tomhw)
Trusted Member
Joined: 2 years ago
Posts: 44
 

There's your problem. An ET 200SP needs the server module on the end, the small grey thing that comes in the box with the IM, it closes the backplane bus. Without it the bus is open and the station never comes up, so every slot reads missing.

Look in the IM box, it's usually under the paperwork. Clip it onto the last BaseUnit, power cycle, and the IM goes green. It doesn't appear in the hardware config, V18 assumes it's there.



   
ReplyQuote
(@fee_m)
Trusted Member
Joined: 1 year ago
Posts: 33
Topic starter  

Found it in the IM box under the leaflet, exactly where you said. Clipped it on, power cycle, IM green, all six modules green, conveyor section running.

So there was no server module on the end of the rail and the backplane was open, and clipping it on was the whole job. Firmware had nothing to do with it, my guess was wrong.

I still don't get why the buffer says backplane error instead of telling me the server module is missing. Maybe the IM can't tell the difference. Thanks tomhw and dieter_k.



   
ReplyQuote
(@dieter_k)
Eminent Member
Joined: 2 years ago
Posts: 20
 

Every first ET 200SP. Mine hid in the packaging for a day.



   