Forum

Light curtain OSSD ...
 
Notifications
Clear all

[Solved] Light curtain OSSD into a 1769-IQ16 chatters every few seconds, curtain never trips

8 Posts
3 Users
0 Reactions
166 Views
(@paul73)
New Member
Joined: 2 years ago
Posts: 0
Topic starter   [#66]

Case sealer. Light curtain on the infeed, OSSD1 and OSSD2 into a 440R safety relay. Standard PLC is a 1769-L33ER with a PanelView Plus 7 on the front.

Operators see a "CURTAIN BLOCKED" banner blink on and off for a fraction of a second every few seconds, all shift, nobody near the curtain. The curtain itself never trips, the relay never drops, the line keeps running. It's just the screen, but the operators have stopped trusting it.

That banner comes off an IQ16 input, where somebody before my time teed OSSD1 at the terminal strip into a spare point so the standard PLC knows the curtain state.

So I power cycled the cell twice and moved the tee to a different IQ16 point, same blink either way.

Is the curtain on its way out? It's ten years old. Any ideas before I price a new one?


Advertisement

   
Quote
(@redgum)
New Member
Joined: 2 years ago
Posts: 0
 

How often exactly, and what's the input filter on that IQ16 point? "Every few seconds" sounds like a schedule, not a fault.


Advertisement

   
ReplyQuote
(@paul73)
New Member
Joined: 2 years ago
Posts: 0
Topic starter  

watched it with a stopwatch, every four or five seconds, same each time. Filter I've no idea, whatever the card does out of the box.



   
ReplyQuote
(@danr40)
New Member
Joined: 2 years ago
Posts: 0
 

The curtain is checking itself, and it's fine. OSSD outputs drop low for a very short pulse every so often, that's how the curtain proves the output stage and wiring aren't shorted. The 440R input is built to ignore that pulse. The IQ16 isn't, it sees a zero for a blink, and your banner follows it.

Two things. Most curtains have a separate status or aux output that isn't pulse tested, meant for a standard PLC wanting the state. Use that into the IQ16. And take the tee off OSSD1. A standard PLC wire on a safety channel is a place for a fault to sit that nobody tests. A longer input filter would probably hide the blink, but hiding isn't the fix.



   
ReplyQuote
(@paul73)
New Member
Joined: 2 years ago
Posts: 0
Topic starter  

Curtain connector has an "aux" pin, the drawing says unused. So the aux goes to the IQ16 and the tee comes off, I think. Do I need anything between?



   
ReplyQuote
(@redgum)
New Member
Joined: 2 years ago
Posts: 0
 

Nothing between. Aux to the IQ16, tee off, banner tag stays the same.



   
ReplyQuote
(@paul73)
New Member
Joined: 2 years ago
Posts: 0
Topic starter  

Ran a wire from the aux pin to the IQ16 point, pulled the tee off OSSD1 at the strip. Banner solid all shift, only shows when somebody actually walks through the curtain. Operators are happy, or as happy as they get.

Ten year old curtain and nothing wrong with it. The blink was its own test pulse on the OSSD and the IQ16 was reading it as a real drop. Aux output for the standard PLC, OSSDs going nowhere but the relay, and the tee is off the strip.

What I still don't know is why nobody noticed the blink before my time. Either it did and somebody lived with it, or maybe that point had a longer filter on it once. Thanks danr40 and redgum.



   
ReplyQuote
(@danr40)
New Member
Joined: 2 years ago
Posts: 0
 

The curtain was telling you it was working. Every few seconds.



   
ReplyQuote
Share: